Important note here: a GFI (ground fault interrupter) outlet is not a
circuit breaker!  It will not save you from an electrical meltdown (or
fire) if you overload your 115 volt circuit.  What a GFI does do is
check to make sure that the outgoing current on the black (or hot) wire
is exactly the same as that passing through the white (or neutral) wire.
If any current finds a path to ground by any other route, such as
through your body, the GFI senses a disparity in current between hot and
neutral, and opens the circuit within a small fraction of a second,
protecting you from electrocution.
Short story: you still need a 15 amp breaker.