| Subject: | RE: Clean Fire Extinguishers |
| From: | Mark Howser |
| Date: | Tue, 30 Apr 1996 08:44:09 -0700 |
Ken,
Unfortunately, you won't find a fire extinguisher that effectively stops =
the fire and remains clean at the same time. Fire is the result of a =
chain reaction involving an increase in temperature, availability of =
fuel and an adequate supply of oxygen for combustion purposes.
To extiguish a fire, interrupt the essential elements of fire. Doing =
one of these will extinguish the flame.
1. Reduce the temp.
2. Remove the fuel.
3. Exclude O2.
4. Stop the Unihibited Chain Reaction (Note: This method is effective =
on gas =20
and liquid fuels b/c they must flame to burn. This is where your =
Halon fire extiguisher comes in. The Halon (hologenated =
hydrocarbon) replaces the O2 which causes the fire to stop flaming. =
However, smoldering fires are not easily extinguished, b/c the moment =
the Halon is shut off, air again has access to the smoldering fuel and =
reignites, continuing to burn.
Types of Extinguishers:
Class A: Ordinary Combustibles (wood, paper, rubber, plastic)
Class B: Flammable Liquids (liquids, greases, gases)
Class C: Electrical Equipment (live electrical equipment)
Class D: Combustible Metals (magnesium, titanium, and other "iums")
Class A exting. are rated from 1A to 40A depending on their size. For a =
1A rating 1 1/4 gallons of water are required. A 2A rating requires 2 =
1/2 gallons of water. (see the trend?)
A dry chemical extiguisher with a rating of 10A is equivalent to five 2 =
1/2 gallon water extinguishers.
Class B extinguishers are rated from 1B to 640B. A complicated UL =
rating system best described by "...the 60B extiguisher will =
effectively extinguish a sixty square foot fire when used by a non =
expert...."
Class C refers to whether the extiguishing agent conducts electricity. =
You wouldn't want to spray a flaming engine with a class A fire =
extinguisher unless you wanted to chance shock or electrocution.
Class D--you aren't going to effectively stop the spread of burning =
metals with any portable extinguisher. Call the FD, EPA and any other =
toxic spill agency that comes to mind.
A fire extinguisher is rated as follows.
4A 20B:C
This extinguisher should extinguish a Class A fire that is four times =
larger than a class 1A fire, extinguish approx. 20 sq/ft of class B fire =
and is also safe to use on energized equipment.
Good luck,
Mark
80 Westy
East Glacier Volunteer Fire DepartmentHave something to add on this topic today? Revive this thread in the forum »